|
|||||||
Remodeling or Building Got a project going or finished... Got a question... |
|
Thread Tools | Display Modes |
#31
|
||||
|
||||
Quote:
Take the blower door off the furnace and see if the airflow doesn't increase. The supply air duct static should be enough to allow the air handler to operate in its normal range. If not, cover the blower door opening about half way to introduce a little more static. Convoluted blowers need some static. Ken |
#32
|
||||
|
||||
Are we sure the ductwork is intact and /or not restricted/imbalanced?
__________________
Mike Life's journey is not to arrive at the grave safely in a well preserved body, but rather to skid in sideways, totally worn out, shouting '..holy sh*t ....what a ride!' - George Carlin |
#33
|
||||
|
||||
Quote:
Even if the supply duct system meets minimum requirements, often the return duct system will be skimpy, causing the same symptoms. But I think Ricky's is an upflow in a closet; probably with the return created by a raised floor in the mechanical closet. If that's the case, the only way to skimp on this type of return system would be to put small return grille(s) on it. Taking the door off bypasses the return system and air filter. |
|
|